Sorry if treading old ground but I've found past posts with different answers on this (some years old so that may be why!), also I think I may have some other questions depending on the answer!
I know that if you take a non-fused spur from a socket on a ring circuit, you should only take one, and not spur from a spurred socket (the 'only spur from a socket with 2 cables' rule). But I've a couple of questions on the use of FCUs
When putting in an FCU, should it be put in place of the original ring socket, or is it ok after it? i.e:
Or:
Also, is it true that when using an FCU you can spur of a spur more than once?
Thanks!
I know that if you take a non-fused spur from a socket on a ring circuit, you should only take one, and not spur from a spurred socket (the 'only spur from a socket with 2 cables' rule). But I've a couple of questions on the use of FCUs
When putting in an FCU, should it be put in place of the original ring socket, or is it ok after it? i.e:
Or:
Also, is it true that when using an FCU you can spur of a spur more than once?
Thanks!