Any chance of a bigger pic?


Looks to me like a RFC terminated into a CU, with both CPCs joined together, but not actually connected to earth :shock:
 
Also more minor faults:-

Unsheathed cables outside of CU,
No earth sleeving
And I bet that top surface is not IP4X
 
Spot on, RF!

Tried to enlarge image, but just came out too blurry.

Had a lighting circuit giving 120V > E. Opened up to find the lighting circuit cpc attached to the IH cpc....

Noz:

Right,

Right

And right!!
 