BAGGIES1 said:
...On this ring i will require 3 double sockets and some "fused outlet units" for fixed appliances. No spurs will be required.
How many "fused outlet units" should i use as i could have upto 6 for kitchen appliances? What is good practice?
The cooker will be supplied by its exisitng fuse (i'm sure this is a 50a fuse but i will check) on 10mm cable to a isolated Cooker Socket box.
(1) For a kitchen, a good way to do it is to run the ring all round the walls, inside oval plastic conduit, about 150mm above worktop height. You can then put in plenty of sockets and FCUs along it. One every 60cm is not too many. This is very economical in labour and materials. At every position where you have, or ever might have in the future, an under-counter appliance, put a 20A DP switch into the row, feeding a single unswitched socket below. Also put a 5A FCU in this row, feeding a flex outlet next to where you have, or may later have, an extractor fan or cooker hood.
(2) Your cooker MCB is unlikely to be greater than a 40Amp
(3) A cooker switch without a socket is preferable. the socket will reduce the design capacity of the cooker power by 13A. Also, sooner or later someone will plug a kettle into it and drape the flex across the hob so that it gets burned. Also, sockets ought to be on an RCD, and cookers ought not.
(4) If you do not have a split-load CU with plenty of ways already, consider the use of RCBOs.
(5) provide a dedicated 20A radial for your freezer (if you can) that is not on the same RCD as anything else (if at all)
(6) be aware that all your appliances, including the freezer, cooker and under-counters, must have an isolating switch that is in plain view, within 2m of the appliance, and, if not obvious what it does, durably marked.
(7) If you get "the Which book of Wiring and Lighting" or the Readers Digest book, and a copy of the On-Site Guide, you will find they tell you lots of things, and time-saving tricks, and answer questions you didn't know you had to ask. You can buy them or borrow them from your library. They must be version published or revised since 2004, as the regulations changed.
(8 ) Contact your local Authority Building Control dept, and ask what the fees are for inspection of DIY electrics. They ought to have a leaflet. They are supposed to test as well for no additional fee.