- Joined
- 6 Nov 2023
- Messages
- 3,632
- Reaction score
- 1,085
- Country
And what benefit is there in adding/leaving the EP connected?Its got to be less unsafe if the source of the current is protected by an RCD but what harm is there in adding the EP?
Probably because the ';training' seems often to leave a lot to be desired (and/or the individual is not really capable of being 'trained').Why would a trained electrician advise a customer that it was?
Is it worse, as in dangerous, if the EP bonding overall is properly installed?With bonding they become big lumps of earthed metalwork connected to the electrical installation which is much worse.
I am not sure there is an answer to that question because the words do not actually make sense.Is it worse, as in dangerous, if the EP bonding overall is properly installed?
It can be (potentially dangerous) in situations such as flameport described, when a large and touchable metal object is connected to earth (via 'bonding') when it would not be so connected (e.g. because it was a radiator supplied by plastic pipes) in the absence of that bonding.Is it worse, as in dangerous, if the EP bonding overall is properly installed?
Should there be another 'not' or no 'nots'?In that situation, if someone somehow touches something electrically 'live', they will not get a significant shock if they simultaneously touch something 'earthed' (or connected to the installation's neutral). To create (by unnecessary bonding) an unnecessarily earthed large lump of touchable metal therefore increases risk/damaged in that situation.
Well spotted. There's not problem with the "nots", but my fingers typed "if" when they had been told to type "unless".Should there be another 'not' or no 'nots'?
There are, as bernard often reminds us - but it depends upon one's judgement/assessment as to which of two scenarios is the more likely to occur...There are two schools of thought on that....
Yep, if I understand correctly, that's what bernard feels about metal bath. He feels it more likely that something will somehow make a 'floating' bath 'live' than that someone would touch something live whilst also touching an earthed metal bath. By no means everyone would agree with that.If the metalwork is well isolated from earth, with absolutely no chance of becoming live, then it is better that it is not bonded. Where there is any chance of it becoming live, due to fault, or potential error - then it is safer if it is bonded.
I thought the whole point of EP was to equalise the potential in such situations, so that there is no or low shock.It can be (potentially dangerous) in situations such as flameport described, when a large and touchable metal object is connected to earth (via 'bonding') when it would not be so connected (e.g. because it was a radiator supplied by plastic pipes) in the absence of that bonding.
In that situation, if someone somehow touches something electrically 'live', they will not get a significant shockifunless they simultaneously touch something 'earthed' (or connected to the installation's neutral). To create (by unnecessary bonding) an unnecessarily earthed large lump of touchable metal therefore increases risk/damaged in that situation.
If the radiator were supplied by metal pipes, then it is extremely probable that it would already be connected to earth. In that situation, although totally unnecessary,'bonding' it would do no harm.[/S]
It is. If there are two or more items which could have different potentials, they are bonded together to keep them at the same potential.I thought the whole point of EP was to equalise the potential in such situations, so that there is no or low shock.