In this instance, I think the wise thing to do, is to establish what supply fuse rating you have and the load demand on the current distribution/fuse board. But you still do need an electrician.
It would not restrict the power to the heater, but would probably not be sufficiently under-rated to actually 'trip'. However, it could get very hot, and theoretically might 'burst into flames' and/or adversely affect nearby MCBs.
However, in terms of the big picture, I think that the MCB rating is probably among 'the least of the problems'. I would personally say that if you find an electrician who is prepared to run that heater through a 63A MCB (if one is available) in your house CU, that you should consider finding a different electrician!
Kind Regards, John
Hi
Again this was running from my CU in my old house for about 4 years with no problems straight from the fuse box??
No doom or gloom as far as I am concerned! Just do the common sense stuff and not the daft stuff!Yes, I agree and with needing an electrician and asking the DNO but I don't understand all the doom and gloom.
For all we know, the OP may have a huge country pile and there will be no problem.
The design current using nominal voltage is 52.2A12 Kw is considerably more than a shower, 50% more in fact. And that 12Kw rating is at 230 volts.
The same applies to showers.Most likely your supply is actually 240 volts so your power would 13Kw, and current 54.4 amps. It gets worse, you supply is allowed to reach 253 volts, so 14.5 KW and 57.4 amps.
Because, as you go on to say, that is the minimum standard MCB which could be used. I agree that I probably didn't need to add that, since my point, previously stated, is that I personally would not want such a load running from a domestic CU.Why do you say that - "through a 63A MCB"?
That's the point. No, as you know, there are not any 'time restrictions on showers' but, in practice, domestic showers will only be used for relatively short periods, whereas a pool heater (particularly if, as implied, it is an outdoor pool) could well be 'running' for very much longer periods of time.Now it's come down to 12kW, it's not that much bigger than a shower.
Granted, it will run longer than a shower but are there time restrictions on showers?
If it had been deemed acceptable and satisfactory.Would you be 'happy' to have a 12kW outdoor pool heater run from a standard domestic CU (or, indeed, from a 'standard single=phase domestic supply'??
Opinions may vary, but I was saying that I personally wouldn't be all that happy (i.e. would not deem the situation to be particularly 'acceptable {to me} and satisfactory) to have such a load supplied by a 'standard domestic CU' (and the OP seems to imply that it is the only one in the house), even if I lived in Chatsworth.If it had been deemed acceptable and satisfactory. We do not know (I don't think) if the OP lives in Coronation Street or Chatsworth.JohnW2 said:Would you be 'happy' to have a 12kW outdoor pool heater run from a standard domestic CU
Did you read it as 33A? I did when I first looked at it. I think it actually says 53A.The current and kW ratings on the machine are incompatible.