Cable for hob and ovens in new kitchen
4 Mar 2017
We are rewiring our new house as part of a major renovation.
We haven't picked our oven or hob yet and and trying to understand what cabling to put in.
Looking around it seems that typical hop and double oven requirements seem to be around 7kW/31A (hob) & 5kW/22A (ovens).
Do we run one cable (say 10mm) to the hob, then onto the ovens in series (all from one wall switch) - or separate say 6mm cables to each - or 10mm?
Thanks for the help.
It depends on the installation method, but
avoiding conduit and thermal installation, 4mm² and 32A MCB will be fine to supply both.
A lot of people still like 6mm² with the 32A MCB because that's what's always been done because of rewireable fuses which are no longer installed.
Cooking appliances don't use all their parts at once so the design current Is calculated by:
((Total Amps - 10A) x 0.3) + 10A
You have probably overestimated the amperage at 240V but,
53 - 10 = 43 x 0.3 = 12.9 + 10 = 23A
10mm² is often used to supply a whole flat.
Are you personally rewiring your house or contracting an electrician to do so?
I will be using an electrician, but like to know as much as possible before hand and I like to understand what anyone who works in my home is doing. And to understand the questions I need to ask.
And I am generally curious and over think things.
Well one thing you need to know is that your oven and hob won't be in series. They will be in parallel.