Changing hob from gas to electric

Joined
23 Jan 2003
Messages
285
Reaction score
3
Country
United Kingdom
Currently I have a gas hob and want to change to electric.
The electric oven is hard wired (6mm & 32A mcb) and a dedicated cooker switch.
Can I run 6mm cable from existing switch to the hob
or
should I replace with double cooker switch
or
do I need a dedicated cable and bcc separate from the oven?
Advice appreciated. Thx
 
Historically, 6mm² has been used for cooker circuits because back when cable was imperial, the size used was 7/0.036" and when cable sizes went metric, the nearest was 6mm².

Also, back then, BS3036 rewireable fuses were very common, & had a higher fusing factor. Because of this, a 0.725 correction factor had to be applied in the current-carrying capacity calc.

Taking this into account meant that 4 milli was too small to carry a 30A load on a rewireable, so 6 milli became the default and it stuck.

In a similar vein, it was later (15th Edition) discovered that 2.5/1.0 T&E was undersized where protected by BS3036, so to rectify this, the circuit was either downgraded by replacing the fuse with a 20A BS3036 or a 30A BS3871 MCB.

By January 1985, it was mandatory to use 2.5/1.5 cable.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top