Constant Tamper Fault on Honeywell PIR
19 Nov 2016
We have a Honyewell Accenta G4 system setup in our house with control panel, 6 x PIR and 3 x door contacts.
A few months ago we were having occasional issues of two of the PIRs setting off the alarm with a tamper fault. I checked ALL of the wiring on both the PIR ends and the Control Panel and all was correct and solid.
So eventually i put a loop into the tamper circuit on the control panel just on the PIRs so that i would effectively turn off the tamper just for the interal PIRs.
It was then all fine for months.
Then yesterday the alarm was set off again at 5am with a tamper fault on one of the internal PIRs, which should not be possible.
Does anyone know what i should do?
I will check the wiring again and will look into replacing the PIR or maybe even replacing the Circuit Board in the control panel.
Cheers
19 Nov 2016
how do you know it was from one of the pirs, given that you linked out a global tamper?
Thanks for your reply. I know it's one specific PIR, as the keyboard says Tamper Fault Connection #3 on the screen.
Connection #3 is a single PIR.
The false alarms have always been either Connection #3 and #5 which are both internal PIRs.
We've never had faults with either keyboard or either bell box which are on seperate tamper circuits.
16 Feb 2011
Sheffield
Didn't think the accenta did eol on each zones ? So how your getting a tamper on a certain zone is a mystery?
20 Jun 2014
Lancashire
I am struggling to understand how you could loop out tampers in the alarm panel for a specific device.
the way alarm panels work is they use a
:global tamper (normally closed) the tampers from each device linked in series (this will not give a device specific tamper error)
:a zone alarm and zone tamper (double pole) this will give a separate zone tamper.
:resistors, two wires like normally closed but the resistances are used to determine if a zone is in alarm or in tamper. this will give a separate tamper.
19 Nov 2016
I have looked on the system Log again, and maybe i was wrong.
If is saying "F" under zone 3 and everything else including TP is set at 0.
20 Jun 2014
Lancashire
okay, so all this tells me is zone 3 was the first to trigger and only zone 3.
so you set the alarm on an evening and where are zones 3 and 5 located?
19 Nov 2016
Zone 3 is in the middle of the house (living room). All externals doors have contacts and there is no way to get to that without passing other rooms / PIRs.
So F doesn't mean fault??
20 Jun 2014
Lancashire
the answer according to manual is not, if any subsequent zones are activated it is didplayed as a 1.
so zone 3 followed by zone 5 would be;-
12345678 TP
00F01000 00
