High Integrity Earthing
1 May 2003
Durham
I understand the principle of high integrity earthing at sockets when protecting sensitive equipment.
But what happens when you get back to the CU and "circuit 2's" CPC's should be in space # 2 on the CU earth bar. Should those be split? Should that earth bar have 2 connections, again, onto the main incoming supply? How far do you go?
Am I just on an adrenalin rush through alcohol and Italy beating France?
Or am I thinking to hard on a day off??
As the connection from the CU to the mains (or submain) is likely to be larger than 10mm, you would not need to have two connections here.
You do need to split the two earths of the circuit at the DB (and fit a warning sticker), so would use two terminals. If there are not enough terminals, you can share terminals with adjacent circuits. Not ideal, but better to share that way than put them both in the same terminal. If you have two or three circuits that have high integrity earthing, you can simply swap the earths around (so to speak) so that only the circuits with high integrity earthing have their earths in odd places (with each other). You should label the conductors.
High integrity earthing is not "for sensitive equipment" - It is for safety, should an earthing conductor become detached, and then end up with volts floating on it due to the higher than normal earth leakage of attached equipment.
Thanks for clearing my Sunday brain hurt thoughts!
Just someone said to me earlier that "if the earth's are separate at the socket, why doesn't that new CU have 2 "#2's, 3's etc." on the earth bar."
I was flummoxed so shut him up by buying him a bevvy!!
High integrity earthing is not "for sensitive equipment".
I think that's just the way it was put to us at college.