Referring to notes from 2012 re a panel fault of devices 'dropping out' and 'breakers tripping':
24V 750VA Park (PES) transformer, primary MCB 6C,
With no sec load I had to operate the pri MCB 4 times before it held in. referring to MI’s - changed to16D.
Pri voltage 243V, OFF LOAD pri current 0.45A (approx 100VA)
OFF LOAD Sec voltage 27.7V
4.8A – 25.6V
7.2A – 25.5V
9.7A – 25.5V
12.7A – 25.5V
17.3A – 25.5V
22.8A – 25.5V
26.2A – 25.5V
31.0A – 25.5V
34.6A – 25.5V
38.6A – 25.5V
42.1A – 25.5V
46.2A – 25.4V
Ie the regulation from 25% to 135% is pretty much flat according to a meter with a 0.1V resolution.
However they are quite inefficient as seen by the offload current which does improve with load.