It's true that there can't be that sort of issue with RCBOs. However, when I raised the neutral bar issue, I was thinking of a situation in which the errant RCBOs were connected to a 'neutral' bar different from the one the other RCBOs were connected to AND that first 'neutral' bar was not actually connected satisfactory to neutral.You can get away with one single neutral bar if all circuits are on RCBOs - so there wouldn't be an issue of connecting a circuit to the wrong neutral bar........like there can be with two RCDs covering a number of circuits each.Why can't it be a neutral bar issue ? Not sure what is special about RCBOs vs MCBs in this respect - you still need a neutral on each circuit.
As you say, Simon is not being totally clear. As I said, if he meant that both L&N of the load had been disconnected from the RCBO, then I can see nothing other than a faulty RCBO that could render it 'unsettable'.The only reason that I can think of that an RCBO would trip without a load (line conductor) connected to it would be a neutral/earth fault on that circuit - but the other circuits would have to be under load.
Ah, I see what you are getting at.You can get away with one single neutral bar if all circuits are on RCBOs - so there wouldn't be an issue of connecting a circuit to the wrong neutral bar........like there can be with two RCDs covering a number of circuits each.
Go back and read the original description.I'm not following what you are testing for here?? Is it me? What test are you performing?
You're not being very clear, I'm afraid.![]()
This is, indeed, getting very frustrating! If you're seeing voltage between the RCBOs' L output and 'the main neutral terminal', but not between the RCBOs L & N outputs then either the RCBO is faulty (no continuity between N input and N output when set) OR the neutral (bar) to which the RCBO is connected is not actually at neutral potential. I can see no other possibilities.So you've got an RCBO connected to the live bar, it's blue wire is connected to it's place in a neutral bar, there is no connected load wiring (neutral or line), the breaker has set, but you get no supply from it's load terminals. And it's not just one RCBO, there's two of them doing the same thing.
If you are following, by now you are probably thinking, as I did, that there's a fault in the breakers.
I put one side of the indicator on the main neutral terminal, got a light from the live bar terminal on the breaker, touching the live load terminal made the breaker trip (my indicator takes enough current to do that).
When I tried probing between live bar and the breaker neutral load terminal, I got ... nothing.
but worrying all the same and it'll be reported to the supplier as a product safety issue rather than just a faulty item.
In that case, I reckon I'll give myself a little creditWell two of you have spotted the fault now. Difficult giving enough information but without giving the game away too easily... One of the neutral bars wasn't in fact connected to the main neutral terminal on the incomer switch
Hmmm - from what you've said, it sounds as if RCBOs 6, 7 and 8 were probably connected to a different neutral bar from 1-5 - and one wonders what was feeding the 6/7/8 neutral bar (and what potential it was at).
True, I didn't explicitly answer that - but I think it's implicit in what I said in that first contribution that the first thing I would have done would have been to investigate what, if anything, the 6/7/8 neutral bar was actually connected to!Interesting that in spite of several times asking "what would you test/do next ?", there were very few suggestions on that front.
True. But then it would have spoiled it for the rest to give the game away too soon.In that case, I reckon I'll give myself a little credit, since my first contribution to this thread was:
Yes. I suspected that my initial suggestion was probably more-or-less right from the fact that your response to my comment was conspicuous by its absence, whereas you responded to most other people! I guess it all goes to show that non-electricians have been known to have their usesTrue. But then it would have spoiled it for the rest to give the game away too soon.
Indeed, it's partially a consequence of the teaching/practice that there should be no visible copper. I have to say that (despite the flak it may cause), I have always try to adopt the opposite practice - i.e. to be sure that there is always a tiny bit of bare copper visible, to reassure me that I have indeed tightened onto copper, rather than insulation.I guess the main lesson I learned (or rather, was reminded of) is don't take the simple things for granted. The link between the neutral bars was there, the screws were tight, what could possible go wrong with a bit of copper bar and two screws![]()
... The neutral bar is split and has a link between the sections in the non-split boards...
No money needed - the 'honour' is adequate - but I suppose you could touch bthe 'Thanks' button if you wanted toDoes JohnW win 50p for being the first pretty much spot on?
Kind Regards, John.