I imagine some of you may well spot the answer very quickly, but here goes ...
Background. A colleague is doing some work in his new (to him) house (which is still empty at the moment). One of the task is to fit a new consumer unit - which is something I would have done for him if it weren't for the LABC fees to notify.
At the weekend I took the old Wylex fuse board off, moved the base board a little, tidied up the cables (in trunking instead of grey stripy wallpaper), etc. To avoid any surprises, I did IR checks (all in excess of 10M both L-N and L+N to CPC) and loop resistance of the RFCs. So no surprises expected.
Friendly spark came to fit new CU on Tuesday, and all went well until he came to test the last few breakers (all RCBOs). Ccts 1 to 5 were all OK. Cct6 wouldn't set - breaker just tripped free immediately.
Ccts 7 & 8 were odd, the tester (Metrel ?) just beeped and displayed "PE" on the display.
The situation didn't change with load wiring disconnected from the breakers.
Consumer unit is this one. Ccts 1-4 are 32A RCBO supplying 3xRFC plus cooker, cct5 16A supplying immersion heater, and ccts 6-8 6A supplying lights.
Yes I know what some people think of these "budget" CUs, that's why I've got spares for the ones I've used in my properties But at those prices, it's not a big premium to go all RCBO.
So based on that, would anyone like to hazard a guess at what fault(s) were present ? Or what to check next ?
Yes, I do know what the faults were, and everything is all fine now.
PS - (especially for B-A-S), please skip the lectures.
Background. A colleague is doing some work in his new (to him) house (which is still empty at the moment). One of the task is to fit a new consumer unit - which is something I would have done for him if it weren't for the LABC fees to notify.
At the weekend I took the old Wylex fuse board off, moved the base board a little, tidied up the cables (in trunking instead of grey stripy wallpaper), etc. To avoid any surprises, I did IR checks (all in excess of 10M both L-N and L+N to CPC) and loop resistance of the RFCs. So no surprises expected.
Friendly spark came to fit new CU on Tuesday, and all went well until he came to test the last few breakers (all RCBOs). Ccts 1 to 5 were all OK. Cct6 wouldn't set - breaker just tripped free immediately.
Ccts 7 & 8 were odd, the tester (Metrel ?) just beeped and displayed "PE" on the display.
The situation didn't change with load wiring disconnected from the breakers.
Consumer unit is this one. Ccts 1-4 are 32A RCBO supplying 3xRFC plus cooker, cct5 16A supplying immersion heater, and ccts 6-8 6A supplying lights.
Yes I know what some people think of these "budget" CUs, that's why I've got spares for the ones I've used in my properties But at those prices, it's not a big premium to go all RCBO.
So based on that, would anyone like to hazard a guess at what fault(s) were present ? Or what to check next ?
Yes, I do know what the faults were, and everything is all fine now.
PS - (especially for B-A-S), please skip the lectures.