Spot the error...

MetalcladCU.jpg
 
Sponsored Links
thats what i meant in my haste to be first :oops:

i'll go to the back and be quiet again :LOL:
 
Sponsored Links
Yup!

A similar problem near the start of the circuit: the T&E cpc was terminated into a conduit box using a very skinny self-tapper into the threaded hole... :eek:

Because of the two high-res earth joints the EFLI at destination was 1086...

The really shocking thing is that these joints have most likely been there since build date: Wimpy, 1984...
 
4mm, red ring crimp on the T+E CPC and a 4mm brass pin, and a pirahnna nut on this end and you're golden... ;)
 
Not quite. No RCD, No discrimination (15A 3036 suuplying garage CU, 15A in garage CU supplying socket)

No bond to water, PME supply & water pipe in garage.
 
no locknut on swa.
no means of earthing, unless PME, then supply swa not isolated from house supply.
old wiring colours.
Fuses are not present.
front cover is missing.
no circuit identifcation present.
 
I don't count old colours as an error tbh
Also not sure on the PME thingy too??
 