Oil boiler lockout - could it be fuel starvation?
18 Sep 2016
We have a Worcester Bosch Danesmoor 20/25 oil boiler that's quite old but has been OK for the 6 years we have lived here. It has on occasion gone into idle mode which I have sorted by pressing the solenoid. However when I tried to turn on the heating a few weeks ago it just locked out after a few minutes andwhen I attempted to reset it the same thing happened continually. The following have been replaced, checked, cleaned but the problem persists:
- replaced thesolenoid, photocell, transformer, burner nozzle and bled the oilpipe, cleaned the filters and the combustion chamber
and all to no availas exactly the same thing is happening, the boiler fires up and thenlocks out after a few minutes. There is a clicking sound (about 8-10 clicks) before lockout occurs.
Has anyone experienced this or have any other potential avenues to explore?
It's getting colderup here in Yorkshire and the missus is becoming somewhat impatient!
26 Jun 2004
London
You seem to have blindly replaced a lot of parts.
You dont mention professional servicing, that makes me think you don't get it serviced which is why you don't seem to have considered what most people would do with a faulty boiler to call an engineer.
7 Feb 2008
Northumberland
It would sound like the burner is igniting then failing as a sequence.....hence the clicking you hear from the control box.
Can you ensure the photocell is actually seeing the flame.....no igniter cables in the way or whatever?
At this stage it's necessary to have the fuel pressure checked and naturally enough, an analysis of the exhaust gases after that.
Have you cleaned the internal flue ways of the boiler at all?
John :)
29 Nov 2009
Shropshire
John is spot on. You are getting re-ignition, then lock out. There may be a problem with the control box which is just about the only component you've not changed, apart from the oil pump.
26 Apr 2011
isle of Lewis
First check oil is getting to burner also check fire valve hasn't operated or failed if it fails it's failsafe
and shuts off if it has you can check by tying it up very temporary once oil is through check oil pressure at pump needs to be 115/120 if ok check nozzle and photo cell nozzle could be firing
Off centre and cell not seeing light
19 Jul 2007
I can understand "Glaswegian" but I'm fooked by the "Isle of Lewis" translation !!
18 Sep 2016
Thanks guys for the helpful comments. I checked the pressure and it's correct at 105 psi and the photocell has a clear view of the flame. The pressure gauge showed that after about 2 minutes the pressure suddenly disappears and the burner re-attempts to ignite what is now presumably a nozzle starved of oil. Lockout follows and i'm left still scratching my head. Any more thoughts - why would the oil pump pressure always drop around about 2 minutes...? Cheers, Phil.
29 Nov 2009
Shropshire
Check the oil line for blockage, especially filters. If the filter is clear, make sure it is bled properly. The burner runs with what is in the pipe, but it is not being replaced quickly enough. When left, it fills up slowly which allows your 2 mins run time.
26 Apr 2011
isle of Lewis
Ok so you've cleaned the filters did you change the actual filter
you have set the oil pressure at 105 that is 25kw setting so you should have a 0.75 x80degree EH
Nozzle the air should be about 6 make sure you have a good flow of oil if you have then you may need a new pump.To get 25kw there is another setting 120psi .6x80degreeS
6 Sep 2010
Avon
Check that the drive dog (the plastic connecter between the oil pump and motor) is not worn causing it to slip on the spindles??!!