Just bought a new belling oven. It's a 12kw oven. We have a 6mm T+E cable feeding the old oven but the new oven says to use flexible cable. What cable would you use and what's the best way to connect to the terminal, ring crimp or bend wire around screw.
Personally I'd disregard that and use your existing t and e. Those screws have a square washer to clamp the cable so it's not necessary to wrap it (and would be quite difficult to do). Just make sure the outer sheath is clamped securely at the bottom, and double the earth over so it's not the first to get pulled out.
Edited to add - I mean the outer sheath of the cable at the bottom of the junction box, not the insulation of the core going into the terminal