Replacing Honeywell cm921 with Hive

Discussion in 'Plumbing and Central Heating' started by Hopeless diyer, 11 Jan 2020.

  1. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    Looking for some help / guidance to replace our existing Honeywell cm921 thermostat with a Hive. I've removed the faceplate and there is a red wire connected to A a yellow wire connected to B and a blue wire going to one end of a terminal. I can also see a green/yellow wire behind this not connected to anything.

    Would I be correct in wiring the hive as follows?

    Blue to N
    Red to L + a loop from L into 1
    Yellow to 3
    Green/yellow to earth


    20200111_133444.jpg
     
  2. Sponsored Links
  3. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,155
    Thanks Received:
    1,408
    Location:
    North
    Country:
    United Kingdom
    You need to establish whether they’re connected to 230vac or 24vac. Is it a combi boiler you have?
     
  4. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    Yup combi, it's a vaillant ecotec pro 28.
     
  5. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,155
    Thanks Received:
    1,408
    Location:
    North
    Country:
    United Kingdom
    So it could be 24v or 230v, connect it wrong and you’re looking at around £150 for a new pcb. Do you have a multimeter or a voltage tester?
     
  6. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    No, if I get one what am I testing it for?
     
  7. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,155
    Thanks Received:
    1,408
    Location:
    North
    Country:
    United Kingdom
    What voltage is present
     
  8. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    Okay I'll check tomorrow and update here.
     
    • Thanks Thanks x 1
  9. Sponsored Links
  10. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    So checked with multimeter and voltage difference between the red & yellow is 204.
     
  11. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,143
    Thanks Received:
    1,567
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    It does seem likely it is 230 volt control with that voltage, the coil of a relay or other item on PCB will likely account for volt drop, however you don't know if neutral is connected would expect two other voltage readings yellow to blue and red to blue would expect one with show full 230 volt showing that is line feed. (Expect it will be red)

    Personally I would not trust meter readings I would want to look in boiler, however I have been told with some boilers to get to terminals means breaking a gas seal, so can see why some rely on readings.

    So very likely blue to N red to L with link to 1 and yellow to 3 assuming a single channel Hive. And the green/yellow to earth tether.
     
    • Like Like x 1
  12. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    So to confirm red is live feed should I take a reading from red to the blue that's in the terminal bloc and confirm it's reading the full 230v?
     
  13. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,155
    Thanks Received:
    1,408
    Location:
    North
    Country:
    United Kingdom
    it might be worth it, to go red to blue.
     
  14. Hopeless diyer

    Hopeless diyer

    Joined:
    11 Jan 2020
    Messages:
    7
    Thanks Received:
    1
    Country:
    United Kingdom
    So here are the readings:

    Red to Blue 4v
    Yellow to Blue 244v

    I get the same when testing Red to Earth wire and Yellow to Earth wire.

    I am now thinking Yellow is the live feed and should go to L with link to 1. The Red should go to 3. Does this seem correct?
     
    • Like Like x 1
  15. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,143
    Thanks Received:
    1,567
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    You seem to have worked it out, does seem yellow is feed.
     
    • Like Like x 1
  16. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page