Bowness72 said:
The fuse box has five, 15 amp (blue) and one 30 amp (red) all of which are the old two pronged pull out fuses (if that helps).
Sounds like an old Wylex Standard
When we bought the house about three years ago we were told that it had been "partially" re-wired.
There's a potential mess, right there... it usually means stuff has been added, inexpertly.
Some of the wires coming out of the top of the fusebox look quite new but are next to some which are still covered with very old paint.
And there's one of the indicators, right there. You can't cable into the top of an old fusebox and retain the degree of ingress ('international') protection required without resorting to some form of mastic.
I dont think there is a problem with earthing, we had a visit from the electric man who did something with that next to the junction box.
Even if he has upgraded your cutout he wouldn't have connected the earth conductor, which you may not even have. They never do.
Other things you
may find:
No earth on lighting circuit
Incorrectly fused lights (smallest fuse is 15A, right?)
incorrectly identified circuits - if identification exists at all
Rats nest inside the fuseboard
Mix of cable sizes/multiple circuits sharing fuses
No RCD protection, of course
No supplementary bonding in the bathroom
Undersized main equipotential bonding (along with, I suspect, no actual connection to the means of earthing)
(If the earthing is not up to scratch it means that you have no protection from live-to-earth faults becaue the automatic disconection won't work. )
None of these things mean it is immediately dangerous (except for the lack of an earth) just that it probably falls a long way short of compliance, like the majority of domestic installations. But you shouldn't consider altering any of it until you know what you're dealing with.
Professionally I should recommend a Periodic Inspection Report, but this may be an expensive way of finding out you need a rewire. You could ask a couple of electricians for quotes to do the work you're thinking of. If they don't check the earthing and bonding and talk about certification and the Building Regulations then don't consier employing them.