3 core and earth sockets

Discussion in 'Electrics UK' started by Tactical DIY, 10 Jul 2021.

  1. Tactical DIY

    Tactical DIY

    Joined:
    5 Apr 2021
    Messages:
    15
    Thanks Received:
    0
    Country:
    United Kingdom
    Hello,
    My house has 2.5mm 3 core and earth for the sockets. I'm adding an extra couple of sockets and want to make sure I'm using the correct cables.
    Can someone confirm where the earth goes and which of the 3 "cores" are used as the live and neutral when wiring a new twin socket?
    Thanks
     
  2. Sponsored Links
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,154
    Thanks Received:
    1,290
    Country:
    United Kingdom
    Can you post some pictures of your sockets and cables please?

    Pictures speak a thousand words.
     
  4. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    74,264
    Thanks Received:
    4,290
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    that's very odd.

    What colour are the three cores, and how have you verified they are 2.5mm?

    They're not lighting sockets, are they?

    photos would be interesting.
     
  5. Tactical DIY

    Tactical DIY

    Joined:
    5 Apr 2021
    Messages:
    15
    Thanks Received:
    0
    Country:
    United Kingdom
    It's definitely the "plug" sockets as I took the faceplate off.
    The cable is 6243Y 3x1.5+1
    Separate wires are
    • Bare copper with a green and yellow sheath
    • Grey
    • Brown
    • Black
     
  6. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    74,264
    Thanks Received:
    4,290
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    and you are in the UK?
     
  7. Tactical DIY

    Tactical DIY

    Joined:
    5 Apr 2021
    Messages:
    15
    Thanks Received:
    0
    Country:
    United Kingdom
    Yeah.
    When I took the faceplate off it definitely puzzled me.
     
  8. Tactical DIY

    Tactical DIY

    Joined:
    5 Apr 2021
    Messages:
    15
    Thanks Received:
    0
    Country:
    United Kingdom
    I'll get photo tomorrow when I'm back at the house.
    I just noted down the size and colours
    The cable is 6243Y 3x1.5+1
    Separate wires are
    Bare copper with a green and yellow sheath
    Green
    Brown
    Black


    Read more: https://www.diynot.com/diy/threads/3-core-and-earth-sockets.574272/#ixzz70F1IRnGeknyhe
     
  9. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    74,264
    Thanks Received:
    4,290
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    might have been wired by an industrial electrician who stole the cable from work.

    Although there are conventions for colours, you can't be sure what he has done. You need to look in the CU, and then to test at each outlet.
     
    • Thanks Thanks x 1
  10. Sponsored Links
  11. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    74,264
    Thanks Received:
    4,290
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    that's lighting cable, not for sockets.
     
  12. Tactical DIY

    Tactical DIY

    Joined:
    5 Apr 2021
    Messages:
    15
    Thanks Received:
    0
    Country:
    United Kingdom
    That sounds very likely as the previous tenant worked as a spark at a factory.

    I'll remove some further faceplates and see what he's done with them.

    On speaking with the spark who connected my supply for an outside building, he said as long as you know what wire he hasn't used from the 3 (grey/brown/black) then I will know what he's used as the circuit/ring.

    Does that make sense!?
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,456
    Thanks Received:
    4,203
    Location:
    Retired to:
    Country:
    Portugal
    No such thing.

    1.5mm² T(hree)&E may be used for sockets and 1mm² T&E or smaller flex used for lights.
     
    • Thanks Thanks x 1
  14. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,591
    Thanks Received:
    377
    Country:
    United Kingdom
    So you are now saying the cable is 1.5mm² not 2.5mm², that is more believable (while 2.5mm² 3+E exists it's not exactly common).

    It's not wrong per-se to use 3+E and leave a core unused or doubled-up, but the use of a cable that would normally be used for lighting on socket circuits raises questions of whether there is adequate over current protection. You really need to fully investigate the situation before you can make a plan on how to go forward.

    What terminals are the wires connected to in the existing sockets? is there any tape or sleeving applied to identify the conductors? is the use of the colors consistent throughout the circuit?

    What fuse or breaker are these sockets fed from?

    Is the 3+E present throughout the whole circuit or just for part of it?
     
  15. Tactical DIY

    Tactical DIY

    Joined:
    5 Apr 2021
    Messages:
    15
    Thanks Received:
    0
    Country:
    United Kingdom
    That was my mistake with the 2.5. Fat fingers.
    It is 1.5.
    When I'm back tomorrow I'll check what terminals are used for the relevant colours and let you all know.
    I'll also check the breaker, but I'm sure it is a 16a.
     
  16. Astra99

    Astra99

    Joined:
    1 Feb 2011
    Messages:
    902
    Thanks Received:
    144
    Location:
    Gloucestershire
    Country:
    United Kingdom
    1.5mm² T(hree) & E is rated at 20A clipped direct, so IF the circuit breaker is rated at 16A, there is nothing to prevent 1.5mm² being used for a radial socket circuit, is there?
     
    • Thanks Thanks x 1
  17. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,456
    Thanks Received:
    4,203
    Location:
    Retired to:
    Country:
    Portugal
    No, nor is there anything to prevent it being used on a 32A ring.

    It satisfies the minimum CCC of 20A (if installation method appropriate).
     