EICR just 2 faults:
'Lighting circuit incorrect RCBO rating, incorrectly labelled - C1'
'Cooker circuit incorrect RCBO rating, incorrectly labelled - C3'
Being the pratt I am I didn't take my phone so no pictures but only went see what make was required.
CU: 6 way all RCBO, beautifully labelled with Dymo.
Tenant demonstrated that 3 rings on the hob trips the 6A RCBO labelled 'Lights', he says it's only been happening since the inspection on 5th Nov.
I flicked the 32A RCBO labelled 'Oven' off and the lights above went off.
Inside it was beautifully wired except the 2 circuits in question look to be crossed over (the shower RCBO is in between them and the brown/blues have obviousely been disturbed and crossover the shower cable), as soon as I restored them to the correct RCBOs and redressed they looked just like the rest, all neat and regimented. I did IR. Loop and RCD tests which were close enough to the EICR.
The estimate attatched to the EICR is for £182 plus VAT to replace the wrong RCBOs...
'Lighting circuit incorrect RCBO rating, incorrectly labelled - C1'
'Cooker circuit incorrect RCBO rating, incorrectly labelled - C3'
Being the pratt I am I didn't take my phone so no pictures but only went see what make was required.
CU: 6 way all RCBO, beautifully labelled with Dymo.
Tenant demonstrated that 3 rings on the hob trips the 6A RCBO labelled 'Lights', he says it's only been happening since the inspection on 5th Nov.
I flicked the 32A RCBO labelled 'Oven' off and the lights above went off.
Inside it was beautifully wired except the 2 circuits in question look to be crossed over (the shower RCBO is in between them and the brown/blues have obviousely been disturbed and crossover the shower cable), as soon as I restored them to the correct RCBOs and redressed they looked just like the rest, all neat and regimented. I did IR. Loop and RCD tests which were close enough to the EICR.
The estimate attatched to the EICR is for £182 plus VAT to replace the wrong RCBOs...