Why not just run them at 110V like they're designed for?
HI
Why not just run them at 110V like they're designed for?
Because every time i run a 110v transformer it always trips some thing it the Shed or house.
I'm looking on running 40W bulbs on a 100m set with 33 lamp holders.
what transformer would i need i think a 1000KA??
It would be odd for a 110v site transformer to trip a B32. Either your circuits are already highly loaded, it's an unusually large transformer, or the circuits are protected by a relatively small/overly sensitive MCB.
Hmm.what transformer would i need i think a 1000KA??
Hmm.what transformer would i need i think a 1000KA??
1000KA @ 110V.
Too big for the public supply - you'll need a generator.
Have you got somewhere you could put something like this?:
Sorry - couldn't resist....