here you go Reg 8
Regulation 8 Existing gas fittings
(1) No person shall make any alteration to any premises in which a gas
fitting or gas storage vessel is fitted if that alteration would adversely affect the
safety of the fitting or vessel in such a manner that, if the fitting or the vessel had
been installed after the alteration, there would have been a contravention of, or
failure to comply with, these Regulations.
82 This regulation embraces a wide range of physical alterations to premises that
might affect the safety of an existing gas fitting or gas storage vessel installed in the
premises where the alteration is to be made (see paragraph 87). Before a significant
alteration is made to premises where a gas appliance is installed, eg installation
or removal of windows, air bricks, extractor fan units etc, any implications for gas
appliance/fitting safety need to be properly addressed (see paragraphs 83-87).
Similarly, prior consideration needs to be given to the possible effect of any
modification, such as a building extension, on the safety of a gas storage vessel
(eg from any reduction in separation distances and standards of ventilation), or
on service pipework (for example, the risk of damage to buried pipework from
strain/weight imposed upon it) - see also regulations 6(7)-(8), 7(1) and 19(5).
Requirements of Building Regulations, eg concerning ventilation and flues, should
also be taken into account, as appropriate. Reference should also be made to
Guidance
7(1)
Guidance
7(2)
Guidance
7(3)
Guidance
8(1)
Regulation
7(2)
Regulation
7(3)
Regulation
8(1)
Safety in the installation and use of gas systems and appliances Page 34 of 100
Health and Safety
Executive
regulation 36(11)-(12) concerning duties on landlords in respect of any room to be
converted into sleeping accommodation.
83 Regulation 8(1) applies to householders, builders, gas installers etc, and is
supplementary to any requirements under the Construction (Design and
Management) Regulations 2007. The implications of any change to premises for
safety of a gas fitting or gas storage vessel need to be considered systematically as
part of the overall work planning process.
84 In some cases, the effects of particular work for gas safety may be obvious.
For example, where a chimney is being reduced in height or capped, its
effectiveness in removing flue gases may be drastically affected. Before such work
is started, it needs to be established whether, or not, the chimney is active and, if
so, allowance made for this in the way the work is carried out. This may include
planning for appliances to be disconnected before work commences, preventing
debris falling or being thrown down the chimney, and ensuring appliances are
tested for safety after the work has been completed. (Disconnection/testing of
appliances should only be carried out by someone who is, or is employed by, a
member of an HSE approved class of persons under regulation 3, eg a CORGIregistered
installer.) Similar consideration needs to be given to any proposed
alterations which might affect operation of a flue system, eg fitting a flue liner or
terminal.
85 In other cases, the effects of the work may not be so obvious. For example,
when fitting double glazing or cavity wall insulation, the removal of fixed permanent
ventilation, such as air bricks, and replacement with closeable ventilation louvres (in
contravention of standards) or blockage of vents by insulation material, can lead to
danger from reduced ventilation/incomplete combustion. Equally, fitting extractor
fans can lead to the pull on flues being overcome and flue products being sucked
back into premises. Moreover, the enclosure of an existing flue terminal within a
new extension or conservatory (again in contravention of standards) can lead to flue
gases becoming entrapped.
86 Irrespective of how obvious the implications of the work are for gas safety, the
people involved need to keep these matters in mind, and ensure they are properly
addressed when alterations to premises are planned.
87 Regulation 8(1) applies only to the alteration of premises in which the gas
appliance concerned is installed, ie it does not cover any alteration to adjoining
premises. Gas appliances/storage vessels should be installed so that safety cannot
be affected by any future developments, eg building extensions, on adjoining
property. For example, a flue should be located at a safe distance from any site
boundary, so that in event of any development on a neighbouring site (which could
extend up to the boundary), the flue will continue to operate properly and discharge
of combustion products will not present a hazard to any person (see regulation 27
and Appendix 1).
(2) No person shall do anything which would affect a gas fitting or any flue
or means of ventilation used in connection with the fitting in such a manner that the
subsequent use of the fitting might constitute a danger to any person, except that
this paragraph does not apply to an alteration to premises.
88 This regulation applies to everyone, not just gas installers. It supplements
regulation 8(1), by prohibiting other activities (ie except alteration to premises)
which have the potential to compromise safety; this might for instance include
modifications which cause blockage/obstruction of an air supply vent or flue,
or incorrect installation of an air extraction or condensation control unit. As with
regulation 8(1), it is essential for the implications of any such change or modification
Guidance
8(1)
Regulation
8(2)
Guidance
8(2)
Safety in the installation and use of gas systems and appliances Page 35 of 100
Health and Safety
Executive
to be properly addressed, before work is commenced, to ensure that gas safety
cannot be prejudiced in any way.
89 Modification of any gas fitting should be made only by a competent person
who is, or is employed by, a member of an HSE approved class of persons (eg
CORGI-registered) under regulation 3(3). Alterations not comprising ‘work’ on a gas
fitting but which nevertheless may affect gas safety, eg a change to room ventilation
provisions, should also be made only by a person with the required competence.
Similarly, any significant modification needs to be checked by a competent person
before the gas fitting concerned is taken into use, to ensure that appropriate
standards have been met and safety has not been compromised (see regulation
26(9)).
(3) In relation to any place of work under his control, an employer or a
self-employed person shall ensure, so far as is reasonably practicable, that the
provisions of paragraphs (1) and (2) are complied with.
90 It is recommended that a responsible person, eg a principal contractor,
foreman, site manager or other person with overall control of the work, is
nominated to ensure, so far as is reasonably practicable, compliance with
regulation 8(1) and (2).