But does it actually say that "double socket" in the regs. means a double socket as defined in BS1363?
And I just had another thought while pedantry about what may or may not be connected to a ring spur is being debated. Not that I'd ever want to use one of these things myself, but does BS7671 allow you to put one of these on a spur? It's not just a double socket, after all.....
And I just had another thought while pedantry about what may or may not be connected to a ring spur is being debated. Not that I'd ever want to use one of these things myself, but does BS7671 allow you to put one of these on a spur? It's not just a double socket, after all.....
Oh I see. Well I don't think many of them will actually pull 4.2A across the two USB ports, I think it's limited to 2.1 shared generally. The better quality ones might be a bit meatier.
And wrt that query I'm not too sure. I don't think they're mentioned at all are they? If it confirms to 1363 it must be allowed
That's probably true, but even if they could supply 4.2A at 5V, that would only represent about 91 mA (ignoring inefficiencies/losses) drawn from the 230V supply!
I doubt he means that, but ... if there were a socket (double or single) on an unfused spur of a ring final and someone proposed connecting ('spurring off') a USB charger (or anything else, come to that) to the supply to that socket, would you not tell them that such was 'not allowed'?
BS7671 itself is totally silent on the matter, other than saying that "ring finals, with or without unfused spurs" may supply accessories to BS1363. It is only the guidance of ('informative') Appendix 15 which talks about "only one (single or double) socket" on an unfused spur.
That's probably true, but even if they could supply 4.2A at 5V, that would only represent about 91 mA (ignoring inefficiencies/losses) drawn from the 230V supply!
I just checked the spec and even MK's only draw 2A shared. I have an MK and it's great, wouldn't use any other brand for fear of burning my house down!
BS7671 itself is totally silent on the matter, other than saying that "ring finals, with or without unfused spurs" may supply accessories to BS1363. It is only the guidance of ('informative') Appendix 15 which talks about "only one (single or double) socket" on an unfused spur.
Ah, thanks, I'd forgotten we'd already discussed how that had changed in the current edition. So if that's really only a suggestion, and there's no actual definition of what BS7671 considers to be a double socket anyway, I would have thought that anyone could wire two singles in the same box together and quite definitely claim compliance with BS7671, and possibly even compliance with the "informative" appendix suggestions as well.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local