Depends on the size of the OCD and the current flowing in the fault (arc). An RCD would have tripped tho. 25mm cable in chock block tho?
As I said, not great way of jointing, but yep, 25mm in term blocks :wink:

An RCD may well have tripped, but an RCD on a submain is a sh1te design too 8)
 
I agree Sparks, although you aswel as I know that any circuit should be designed so that a phase earth fault should operate the OCD.

25mm tails into choc block :oops: nice!!
 
A phase to earth short would probably have operated the OCD, however an arc is a different problem!
The poor joint was the start of this problem.
Didn't know it was a submain :(
Depends really on the setup, some submains can have RCDs as long as they discriminate i.e. using type S.
 
i've seen holes you could put your fist through in boxes when things have gone bag in a big way! I should have taken a picture of the 240mm ish lead sheath swa which kicked off between phases due to damp, it burnt two cores completely away. on further investigation the OCB protecting it had a fault on the tripping mechanisam..
 