    Recently had an rsj installed as dinning wall has been removed. Rsj sits on internal skin on a pass time, but only has 80mm bearing on each side? Will this be okay??

    Thanks in advance
     
  2. Sponsored Links
  3. KenGMac

    KenGMac

    Joined:
    24 Aug 2010
    Messages:
    3,355
    Thanks Received:
    634
    Location:
    Ayrshire
    Country:
    United Kingdom
    Jbg123, good evening.

    Any chance of expanding on this please? is it a concrete pad?

    What sort of span does the RSJ cover? and what are the RSJs dimensions?

    Ken
     
  4. Jbg123

    Jbg123

    Joined:
    29 Mar 2019
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Yes on a concrete padstone
    Span is 2850mm
    178x102x19 ub

    Thanks
     
  5. Notch7

    Notch7

    Joined:
    15 Sep 2017
    Messages:
    21,166
    Thanks Received:
    1,459
    Location:
    S. Uplands
    Country:
    United Kingdom
    Your builder has used a 3.0m beam -I would've thought either 100mm or 150mm is usually the minimum (cant remember which)
     
  6. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    9,883
    Thanks Received:
    1,483
    Location:
    Manchester
    Country:
    United Kingdom
    Although you would usually look for a 100 bearing, 80mm will be OK for the loading normally found in a domestic setting.
     
  7. Sponsored Links
  8. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    3,605
    Thanks Received:
    709
    Location:
    Durham
    Country:
    United Kingdom
    Your BCO may want to see some calcs for an 80mm bearing, 150 is standard.
     
  9. noseall

    noseall

    Joined:
    2 Feb 2006
    Messages:
    40,061
    Thanks Received:
    2,519
    Location:
    Staffordshire
    Country:
    United Kingdom
    100mm is standard for steel beams.
     
  10. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    9,883
    Thanks Received:
    1,483
    Location:
    Manchester
    Country:
    United Kingdom
    The crushing strength of the average concrete padstone is around 50 N/mm²; when safety factors are taken into acount, this is reduced to around 20 N/mm².
    If the beam is 102mm wide, and the bearing is 80mm, that gives a contact area of approximately 8,000 mm², so that the maximum load allowed on the padstone surface would be 20 x 8,000 N = approx 160 KN.
    This is way, way above the load that will show in the SEs' calculations for the beam; it is not a problem.
    There are other factors to be taken into account when using a short bearing, but in practice they would not apply in a domestic situation where the loads are relatively low.
     
  11. Notch7

    Notch7

    Joined:
    15 Sep 2017
    Messages:
    21,166
    Thanks Received:
    1,459
    Location:
    S. Uplands
    Country:
    United Kingdom
    Its quite amazing really -it always looks so dodgy when you see a biggish steel with just 100mm bearing -I can see the logic in the maths though.
     
  12. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    30,932
    Thanks Received:
    4,102
    Location:
    West Mids
    Country:
    United Kingdom
    I'll chip in with the ubiquitous "what do the design calculations say"?

    Or are you printing out a thread from DIYnot and submitting it to the council for approval? :cautious:
     
  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page