Firstly:
I REALISE THAT THIS PLUG IS INCORRECTLY & POORLY WIRED AND SO SHOULD NOT REMAIN IN SERVICE.
However, to answer the original question......which I don't think anybody has actually done
If the installation had no RCD & had PME or TNS earthing ... then the appliance would work fine and this error would go undetected. Its also unlikely that this would cause any damage to the equipment, however, should the source of earthing become disconnected then there would be a high risk of electric shock since the incorrect connection would pull all of the "earthed" installation metalwork up towards the phase potential.
*** MY COMMENTS ARE FOR LEARNED TECHNICAL DISCUSSION ONLY. I'M NOT ADVOCATING THAT ANYONE DELIBERATELY WIRE A 3 PIN IN THIS MANNER ***
I REALISE THAT THIS PLUG IS INCORRECTLY & POORLY WIRED AND SO SHOULD NOT REMAIN IN SERVICE.
However, to answer the original question......which I don't think anybody has actually done
If the installation had no RCD & had PME or TNS earthing ... then the appliance would work fine and this error would go undetected. Its also unlikely that this would cause any damage to the equipment, however, should the source of earthing become disconnected then there would be a high risk of electric shock since the incorrect connection would pull all of the "earthed" installation metalwork up towards the phase potential.
*** MY COMMENTS ARE FOR LEARNED TECHNICAL DISCUSSION ONLY. I'M NOT ADVOCATING THAT ANYONE DELIBERATELY WIRE A 3 PIN IN THIS MANNER ***