Saw thanks. Ok so 10mm2 is plenty even with insulation. Future proofed at least in case I end up having to use an all electric cooker.Watch this, it's a good watch.
10mm² yes, but not the type of cable you used.Saw thanks. Ok so 10mm2 is plenty even with insulation. Future proofed at least in case I end up having to use an all electric cooker.
I used a Prysmian 6242Y Grey 10mm² Twin & Earth Cable. Says max operating temp is 70oC.10mm² yes, but not the type of cable you used.
Just put in a 32A RCBO then all is good despite your mistakes.
Ok.I used a Prysmian 6242Y Grey 10mm² Twin & Earth Cable. Says max operating temp is 70oC.
My DP switch has no socket outlet
Yes.That youtube video says "first 10A of rated current plus 30% of remainder"
Yes - near enough.So say I use a 32A RCBO. Then if I use a 12 kW electric cooker (12,000W / 230V = 52.1 A. So using diversity it's 10 A + (52.1 - 10A)x 30% = 10 A +12.63 = 22.63A.
20kW @ 240V is the maximum with 32A MCB/RCBO.I could use a 14kW electric cooker (14,000/230V = 60.8A, diversity it's 10A + ((60.8 - 10A)x30%) = 10 + 15.24 = 25.24A.
16kW electric cooker (16,000 /230V = 69.5A, diversity it's 10A + ((69.5 - 10)x30%) = 10 + 17.86 = 27.86A
Yes, but you must use a 32A MCB/RCBOelectric calc says a 70oC 10mm2 cable is fine with the worst case scenario (any option) of the installation method for a 32A load.
Well yes, either would be ok but, as above, 20kW @ 240V (19.167 @ 230V) is the maximum.So in theory I can get up to 16kW electric cooker. Though 14kW more likely
I already have a 32A RCBO with 6mm2 going to a 45A DP switch. In theory that should be enough to power an electric hob.Ok.
Yes.
Yes - near enough.
Not theory. It is all most dwellings have for the cooker circuit for some reason.I already have a 32A RCBO with 6mm2 going to a 45A DP switch. In theory that should be enough to power an electric hob.
Obviously but it was not needed.So I could use this second 32A RCBO with 10mm22 going to a second 45A DP switch just to power an oven
Or, as above, You could have used the original circuit for any cooking appliances you are likely to get in the future.So I could use the 1st 6mm2 32A cooker outlet to power an electric hob and use the 2nd 10mm2 32A cooker outlet to power an electric oven. Just an idea
I don't have a 17kW oven but I could get oneIt's enough to power the hob and the oven(s).
Have you really got a 17kW+ oven?
Yes, it is an idea.
Whatever other characteristics it may have, it is undeniably an idea.
With a 6mm 32 amp circuit? Yes you could.I don't have a 17kW oven but I could get one
Or with a 10mm2 32amp circuit. Even a 17kw oven off a 10mm2 32A circuit. Lots of potential.With a 6mm 32 amp circuit? Yes you could.
My house only has a 60 amp main fuse thats less than all your cookersOr with a 10mm2 32amp circuit. Even a 17kw oven off a 10mm2 32A circuit. Lots of potential.
"Whatever other characteristics it may have, it is undeniably an idea."It's enough to power the hob and the oven(s).
Yes, it is an idea.
Fair enough. What wire strippers do I need for 10mm2 cables?My house only has a 60 amp main fuse thats less than all your cookers![]()