Dormer loft conversion-Down lights

Discussion in 'Electrics UK' started by Jitno123, 25 May 2017.

  1. Jitno123

    Jitno123

    Joined:
    29 Jan 2017
    Messages:
    41
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi all,

    I'm currently having my loft converted and I plan to have some downlights in the flat roof dormer. Just wondering is the a way to have downlighs without cutting away the celotex? I have seen these 'low profile integrated led' ones which are quite slim. Has any one come across these? I ask as I don't want to cut large holes in the insulation!

    Thanks
     
  2. Sponsored Links
  3. freddiemercurystwin

    freddiemercurystwin

    Joined:
    21 Jan 2007
    Messages:
    18,835
    Thanks Received:
    2,085
    Location:
    Devon
    Country:
    United Kingdom
    Have you the headroom to have a service void?
     
  4. Jitno123

    Jitno123

    Joined:
    29 Jan 2017
    Messages:
    41
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi, by service void do you mean adding a false ceiling? The head room is fairly limited as it is. The joists going into the rsj for the dormer are 120mm, filled with 100mm celotex.

    Is the a way to avoid cutting away at the celotex? Do low profile down lights exist
     
  5. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    7,630
    Thanks Received:
    753
    Location:
    Essex
    Country:
    United Kingdom
    Although the actual led light bit is less than 20mm in some cases, there still needs to be space to accommodate the driver that runs them and that is somewhat bigger and needs a bit of airflow
     
  6. chivers67

    chivers67

    Joined:
    18 Nov 2008
    Messages:
    1,183
    Thanks Received:
    128
    Location:
    Surrey
    Country:
    United Kingdom
  7. bobsuerita

    bobsuerita

    Joined:
    7 Feb 2017
    Messages:
    320
    Thanks Received:
    58
    Country:
    United Kingdom
    whynot go for warm roof or you can get suface mounted ones
     
  8. Sponsored Links
  9. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    16,172
    Thanks Received:
    1,466
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    [​IMG] The lamp holder shown is called a GX53, I have never used one, but clearly a flush mount, it would seem both CFL and LED lamps fit the holder, in other words lamps which do not produce much heat.

    This is one of many options, there are many LED lamps which do not have replaceable bulbs which are more flush than example shown, not sure about the idea of not having a replaceable bulb, but they do seem popular.

    Because a bigger diameter to the 2 inch lamp which sinks into the ceiling likely they would better, 2 inch is really to small.
     
    • Thanks Thanks x 1
  10. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,533
    Thanks Received:
    1,979
    Location:
    Oxfordshire
    Country:
    United Kingdom
    If you chop holes in your insulation your local friendly building inspector will tell you to bloomin well take them out and re-instate the insulation. Or you won't get your building notice signed off.
    The Aurora lights (above) may be a solution but even they need a 40mm free depth.
    Note that the Aurora lights are 4", 5", 6" in diameter.
     
  11. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,489
    Thanks Received:
    917
    Location:
    Dorset
    Country:
    United Kingdom
    I've known builders to construct a special frame within the ceiling joists house spots whilst maintaining some integrity of the celotex.

    How compliant this actually was I couldn't say though.
     
  12. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,315
    Thanks Received:
    876
    Country:
    United Kingdom
    It's compliant as long as the overall u value is good enough, and the worst u value is still better than the limiting u value. Also the vcl has to be sufficient.
    I'd expect the bco to want to see evidence that it's been worked out correctly, but they may or may not.
     
  13. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,533
    Thanks Received:
    1,979
    Location:
    Oxfordshire
    Country:
    United Kingdom
    The only way to do it is to discuss the options with your BCO before you buy or install anything.
     
  14. chappers

    chappers

    Joined:
    27 Aug 2004
    Messages:
    3,254
    Thanks Received:
    357
    Country:
    United Kingdom
    The bottom line is he will never know, in all my days and probably 40 plus loft conversions, I've never seen a BCO pull out down lighters or question if the insulation has been moved.
    I understand your concern though, find some slim LEDs and set the driver/s somewhere remote maybe behind a panel in the wall, or under the eaves.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page