    My boiler - a 15 year old Ideal FF350 - has been starting to play up:

    When it starts up the pilot light will ignite with a loud click, then take a long time to start the main burners, before switching off after 90 seconds or so. After another 90 seconds the sequence will start again and again until the timer switches it off (the boiler will go on and off like this for maybe 10+ times in 20 minutes).

    Is it likely that the solenoid valve is playing up, or a problem with the circuit board? If the valve, for the Ideal boilers, I'm not sure if it requires the "gas valve" or the "gas valve kit classic" (see number 17 on this plumbase page for the boiler). I've been told that if it turns out not to be the valve the PCB will then need to be fixed instead.

    I'm just trying to get an ideal of cost more than anything, especially as this is one of many elusive plumbing problems I seem to have at the moment!

    Thanks in advance

    *********
    Moderator's note
    This site does not support DIY gas and posts giving advice on gas work, or encouraging or suggesting it, may be deleted. However, posts are not routinely monitored, so no work should be done as a result of seeing anything on the site.

    Read more:
    https://www.diynot.com/diy/threads/diy-gas.8090/#ixzz5RjYkglm4
     
    Last edited by a moderator: 21 Sep 2018
  2. Sponsored Links
  3. cross thread

    cross thread

    Joined:
    8 Sep 2005
    Messages:
    1,835
    Thanks Received:
    342
    Location:
    worlds end
    Country:
    United Kingdom
    get a gas engineer in as it sounds like a different reason and a service should sort it
     
  4. ollski

    ollski

    Joined:
    8 Oct 2003
    Messages:
    7,086
    Thanks Received:
    544
    Location:
    Bristol
    Country:
    United Kingdom
    You could do a resistance check on the gv solenoid without risking anything safety wise.
     
  5. gwynant

    gwynant

    Joined:
    21 Sep 2018
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for your replies.

    In that case, the engineer may not be 100% correct in saying that only after fitting a new gas valve (and then not being able to return it) would he be able to deduct whether it was that or the PCB?
     
  6. ollski

    ollski

    Joined:
    8 Oct 2003
    Messages:
    7,086
    Thanks Received:
    544
    Location:
    Bristol
    Country:
    United Kingdom
    to be honest a simple volt pen would go a long way to showing if the power was cutting out from the board but if you were to test live and neutral at the board when it drops out fluctuation would indicate a pcb fault and a steady voltage would probably indicate the gas valve....then you could measure resistance of the solenoids. All diagnosis is pretty simple when you can recreate the fault.
     
  7. Why would you want to recreate the Fault and not find it?....any Fault finding is easy when you find the Fault!
    Any job is easy when you know how,not that easy when you have no idea of volts,amp,dc,farads,millibars,or what component does what,when.
     
    Last edited by a moderator: 22 Sep 2018
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page