Failed EICR-is is justifiable to change RCD box(fuse box)
Iri
31 May 2021
Hello everyone, I need your opinion please. I have got a failed EICR report.
It does not seem right to me, since the fuse box consist of a number of switches, and why electrician wants to replace the whole box? Maybe he is right, but I need your opinions please.
I attach the report.
Also, for a new fuse box he wants to charge £150.00 Must be one of the most expensive on a market.
In his letter:
"Remedial worksElectrical Remedial Works: Works to existing consumer unitMinor rewiring: NoRCD – Residual Current Device: 1 £150. Rcd has failed to disconnet in the stated times and needs replacing with a new one Total Price£180.
Thank you
  • failedeicr.pdf
Assuming that EICR is correct (it isn't), then the only item required is the replacement of an RCD.
Nothing there suggests the whole consumer unit has to be replaced.
£180 would be at the high end of pricing to replace one RCD in a consumer unit.
Replacing the whole consumer unit would be significantly more.
How much did you pay for the EICR, and how long was the person at the property?
is it £150 to fit/replace & £30 for the material RCB
Depending on make/model TLC price is £15-£40
The RCD box is £150.00 and a work of £30.00. He mentioned no rewiring needed
He was about 30-40 mins (it's a small one bedroom flat) and I paid £100.00. I was not present myself, the tenant was there
This is a typical RCD of the type that's been suggested as needing replacement:
Not the whole fusebox / consumer unit.
13 circuits and 40 minutes is 3 minutes per circuit, assuming 100% of the time was spent actually testing and inspecting.
Clearly that is impossible.
I have the feeling that the OP should thank the guy for his EICR and get someone else in.
So he tested 3 RCBO's
And 2 RCDs - 1 of which failed
He's only going to charge £30 labour to replace and produce the necessary PASS paperwork.
So its swings and round-abouts.
Overall it seams you have a good CU layout. And overall cost of EICR and repair isn't bad
It is what it is, but I wonder why the spark fitted 13 circuits in a 1 bed flat?