A
Alarm
Well what do you think? Really?
We have the cable proved as being sound ( as long as you tested correctly)
We have taken the bell trigger away from the bell, and it still sounds (As long as it was wired correctly).
So that leaves one item to be at a known fault.
Tell you what get you test meter on DC range and put one probe on positive and another on bell trigger and see what the voltage is, it should be 0.
Then using bell test , test the bell and repeat and it should read 13.7 or similar.
Will that make you happy?