"653.2 The Report shall include the following:
- - any non-compliance with the requirements of BS 7671 which may give rise to danger"
Appendix 6
An installation which was designed to an
earlier edition of the Regulations and which does not fully comply with the current edition is not necessarily
unsafe for continued use, or requires upgrading. Only damage, deterioration, defects, dangerous conditions
and non-compliance with the requirements of the Regulations, which may give rise to danger, should be
recorded.
Note the word "danger" eg An unearthed lighting circuit has not complied for more than 50 years, and as long as all accessories are plastic it is not dangerous. I would note the fact, advise that metallic accessories and fittings should not be used, and that circuits of that age should be replaced due to hidden deterioration. But it is not a failure
- - any non-compliance with the requirements of BS 7671 which may give rise to danger"
Appendix 6
An installation which was designed to an
earlier edition of the Regulations and which does not fully comply with the current edition is not necessarily
unsafe for continued use, or requires upgrading. Only damage, deterioration, defects, dangerous conditions
and non-compliance with the requirements of the Regulations, which may give rise to danger, should be
recorded.
Note the word "danger" eg An unearthed lighting circuit has not complied for more than 50 years, and as long as all accessories are plastic it is not dangerous. I would note the fact, advise that metallic accessories and fittings should not be used, and that circuits of that age should be replaced due to hidden deterioration. But it is not a failure