A rough sketch where a single bonded water pipe creates a short across the coil. As Flameport has said there are other items whose bonding will create a short
Many thanks for your informative reply Bernard.
A rough sketch where a single bonded water pipe creates a short across the coil. As Flameport has said there are other items whose bonding will create a short
Current doesn't 'build' - it flows depending on the voltage applied and the impedance of what is connected to that voltage source.s would that small amount flowing through the earth electrode build to a level that would eventually trigger the device?
i would say that what flamepotrt didn't fully explain is that it 'depends' - on the nature of the 'E' of the N-E fault, and the presence or otherwise of #'parallel paths' to earth from that 'E'.Thank you for that detailed reply. You say most of the fault current will flow through the N-E connection and very little via the earth electrode. My question is would that small amount flowing through the earth electrode build to a level that would eventually trigger the device?
It does, but it is potentially confusing terminology, given that what causes the device to operate is current flowing through its coil. It operates when the voltage across the coil is equal to the resistance/impedance of its coil multiplied by the current required cause cause a 'trip'.The VO stands for Voltage Operated.
Indeed so - essentially as I said.They were referred to as "Voltage Operated" because they were designed to operate ( trip ) before the voltage difference between CPC and Ground reached 50 Volts which was considered to be a safe voltage. .... The current that was necessary to cause the electro -magnet to trip the mechanism varied depending on the make and model of the VOELCB as they did not all have the same resistance. The only fixed parameter was the 50 Volt hence they were voltage operated when in reality they, like all electro-magnetic devices, were current operated
No, that will never happen.would leaving a working VOELCB in place provide a similar level of safety to an RCD
It would certainly be more likely to work than without such non-conductive inserts, but you still could not rely upon it to offer any 'levelof ssafety' - as flameport has said, since it is inevitably decades old, and relies on moving parts for its proper operation, there's no guarantee that it would work at all when it should, even if the 'electrics' were optimal.Thanks for all your replies chaps. If non conductive inserts on incoming pipes, water and oil in my case and easily installed, were fitted then would leaving a working VOELCB in place provide a similar level of safety to an RCD inside the home.
I nearly mentioned that. If pushing the test button causes it to trip, that obviously means that it was capable of 'working', but it would be wrong to derive too much reassurance from that, not the least because it would tell you nothing about 'reliability' (e.g. whether it would trip every time if you pressed the button several times).Thanks for all that chaps. One further question if I may: If the VOELCB test button trips the power can I take that as proof that the device is serviceable.