    16B6FD32-32C6-42F7-8647-0B805D65E753.jpeg does this look correct ? Im concerned The storage heating runs 24/7 and not just switching on during off peak times. I expected to see a timer or something or does this happen in the meter which has a seperate live feed to the LH consumer unit which supplies the heaters.
     
  2. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    1,687
    Thanks Received:
    75
    Country:
    United Kingdom
    The meter has a tele switch built in to it, what concerns me is the apparent lack of an earth wire going to the off peak consumer unit
     
  3. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    1,817
    Thanks Received:
    86
    Location:
    Kent
    Country:
    United Kingdom
    The switching is done within the meter, the brown wire is correctly wired in as off peak.
    I'm surprised the neutral comes directly from the company fuse but electrically there's nothing wrong with that.
    BUT where is the earth for the off peak consumer unit, I see the green/yellow to the right hand consumer unit but nothing else. I assume you have no gas so that doesn't require bonding but how about the water pipe?

    Edit: I didn't see CB's reply.
     
  4. cider

    cider

    Joined:
    25 Jul 2008
    Messages:
    6,639
    Thanks Received:
    1,282
    Location:
    Bristol
    Country:
    United Kingdom
    Thanks guys. No gas. Im renting. Will look at the earthing (y)
     
  5. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    8,143
    Thanks Received:
    1,493
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    There are other problems:

    Large holes in the top of both consumer units where the cables enter.
    Connector blocks on the supply to the storage heater consumer unit do not appear to be fixed to the wall or anything else.
    None of the grey cables appear to be supported or fixed in any way
    No RCD on the storage heater circuits - which is OK if the cables are all surface mounted. Not if they are concealed in the walls.
     
    • Thanks Thanks x 1
  6. cider

    cider

    Joined:
    25 Jul 2008
    Messages:
    6,639
    Thanks Received:
    1,282
    Location:
    Bristol
    Country:
    United Kingdom
    Definitely no earth between met and off peak board
     
  7. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    4,258
    Thanks Received:
    378
    Location:
    Herefordshire
    Country:
    United Kingdom
    RCD's may not have been required at the time of install.

    Best without them for storage heaters
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page