Perhaps this should be a fresh post or maybe it’s better posted on ARGI Anyway 4/8mb perceptible leak with appliances connected……
Can someone please explain to me why there is a 4mb drop allowed when an imperial (U6) meter is connected and 8mb with a metric (E6) meter. I went to college, I did my ACS and I see myself as more than competent. When this has been explained to me I have been told many different reasons. The most common being that the size of a metric meter is smaller and that it is more or less just a pipe with something to measure the movement of gas. When I have questioned the reasons the explanation usually ends up with ‘because it is’ Trouble is this does not make logical sense to me and it has just become something I accept. So my first question is explain the above…. logically, please.
The second part is this……
Take a hypothetical house with an imperial meter, with a hob, and a boiler (all appliances connected) a tightness test is done and a 5mb drop is found with no smell of gas. Situation is ID and supply is capped. If however the imperial meter was removed and a metric meter put in its place (I’m still in hypothetical house) which of the following would apply
1. The tightness test shows a drop of 5mb, no smell of gas and as such acceptable???? surely not.
2. The tightness test shows a drop of more than 8mb, Situation is ID and supply is capped.
3. Where a new meter is installed the installation is treated as new and as such no drop is allowed (this would apply to Julie Dee) but ruins my hypothetical house
Good Luck
Bob
Perhaps this should be a fresh post or maybe it’s better posted on ARGI Anyway 4/8mb perceptible leak with appliances connected……
Can someone please explain to me why there is a 4mb drop allowed when an imperial (U6) meter is connected and 8mb with a metric (E6) meter. I went to college, I did my ACS and I see myself as more than competent. When this has been explained to me I have been told many different reasons. The most common being that the size of a metric meter is smaller and that it is more or less just a pipe with something to measure the movement of gas. When I have questioned the reasons the explanation usually ends up with ‘because it is’ Trouble is this does not make logical sense to me and it has just become something I accept. So my first question is explain the above…. logically, please.
The second part is this……
Take a hypothetical house with an imperial meter, with a hob, and a boiler (all appliances connected) a tightness test is done and a 5mb drop is found with no smell of gas. Situation is ID and supply is capped. If however the imperial meter was removed and a metric meter put in its place (I’m still in hypothetical house) which of the following would apply
1. The tightness test shows a drop of 5mb, no smell of gas and as such acceptable???? surely not.
2. The tightness test shows a drop of more than 8mb, Situation is ID and supply is capped.
3. Where a new meter is installed the installation is treated as new and as such no drop is allowed (this would apply to Julie Dee) but ruins my hypothetical house
Good Luck
Bob